  1. I believe you are referring to imperfections etc when deigning the falsework. The new DR AS 3610.2 addresses this. It is currently out for public draft. Z36 (mentioned above) is a great design hand book but was published 7 years ago and will need a some updates when it comes to falsework design. The proposed  new formwork standard has a dedicated falsework section.

    Public draft period for DR AS 3610.2 closes 06/04/2021

  2. I would keep having those arguments. The wind load is only appropriate for when installing hoarding on Mars... 

    I don't know what members were on the code committee that put together AS 4687 but my experience of code committees, especially for minor codes that don't attract academics specialised in the relevant industry results in codes that support the suppliers of the product in the given industry. 

  3. Reo cages are truly horrible to model. 

    The number one thing is to model the bars off set from each other or your model will develop too much stiffness. Also model the wire ties as pins. I also carry out tests of the wire tie connections for the particular steel fixer where possible so that some sort of number can be assigned to the ties. You cannot rely on the wire ties for direct structural reliability, but you cannot ignore them either - or you will end up with a very impractical design. 

    I never worry about the displacement as long as the bars remain elastic. It is amazing how large the displacement can get before you start to yield the bars. I highly recommend going to site and watching a reo lift. It will show you what you can get away with in term of deflection and how accurate your modelling is. 

    The big killer for reo cages is the joint strength. Failures on site that I have observed have been distortion/yielding of the 'church' bars (top lifters) owing to inadequate bracing and bar capacity and the welds/wire ties snapping owing to lifting chains binding and applying massive shear loads that were not allowed for. 

    Good luck with reo cage lift design - do not under estimate it!

     

  4. There is no ability in the Australian scaffold industry at this stage to monitor scaffold reuse. The equipment is reused constantly and is discontinued when it can no longer be serviced. Fatigue is not an issue. But the scaffold becomes bent over time and joints are essentially smashed out of shape due to the hammering they take when being done-up and released. 

    Badly bent equipment, especially if in direct compression, must be replaced or reinforced if seen during a site inspection. For engineering I would recommend L/300 out of straight (the allowance for tube in AS3610). Obviously the capacity of the tube must be down graded as steel designed to AS4100 is L/1000. 

  5. AS3610: 1995 has always had the requirement for a 1.3 (30%) increase in FW loads when designing for the strength limit state. AS3610.2 2021 DRAFT also has the requirement for 1.3 LF. This is over and above the 1.25 continuity requirements for a 2 span support. 

    The 1.3 factor is essentially an adjustment between limit state and permissive stress and also based on field studies that showed loads were +/- 30-40% of what was predicted by area tributary methods for determining leg loads. The main reason is for timbers spanning over a support owing to small gaps between jacks and headers. Note that the factor does not need to be applied for single span systems (single joist span and single header span as is the case with most modular systems). 

×
×